1. Welcome to Hvacproforums, an interactive community exclusively for HVAC professionals. The collective years of HVAC experience and the knowledge our forum members share make this an invaluable resource for those in the HVAC industry. We have a lot of fun, but make no mistake, we are pros. Hvacproforums is self supporting ...there are NO advertisers here. Do-it-yourselfers and Homeowners are encouraged to seek information elsewhere. Those involved in the HVAC industry are urged to register. its 100% free and easy, Once registered you will have access to the technical forums, Be sure to click over to the new members forum and introduce yourself after registering!

Headmaster charging

Discussion in 'Refrigeration' started by Texas-Tech, Jul 15, 2012.

  1. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    Had a walkin freezer last week that lost it's compressor, small hermetic. I c/o compressor and fd and recharged. I am under the impression your to add refer till the sight glass clears? When it was done I had head pressure of almost 400psi. I know that's way outa range for 404a and I removed enough to get to 300. Could the headmaster be bad?
  2. Bender

    Bender Promoted to Regional Turd Polisher

    Messages:
    22,744
    Location:
    Mamby Pamby Land
    What was your ambient???
  3. crackertech

    crackertech assholiness

    Messages:
    57,705
    Location:
    Fl/IN

    And box temp?
  4. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    About 79°
  5. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    box was at 35°
  6. Bender

    Bender Promoted to Regional Turd Polisher

    Messages:
    22,744
    Location:
    Mamby Pamby Land
    I don't trust a sight glass until my box is down around operating temps.....

    Was your condenser coil clean? (I've seen quite a few that look clean on the outside but are letting air through)
  7. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    First thing I did was wash it off. Appeared to be clean afterward. My sh outside at the compressor was like 50° also so I went back 2 days later and c/o txv. Then my sh was 17° it was running at 29 & 340psig and the box was at 7 so I left it there.

    Wouldn't you know that sometime after I left the sob shut down on head pressure and no one caught it till the next morning. Man they were pissed.
  8. jpsmith1cm

    jpsmith1cm Professional Un-thawer

    Messages:
    1,056
    400# is way out of line, expecially with a lower ambient like you had.

    http://sporlanonline.com/90-30-1.pdf Here is Sporlan's charging guidelines for systems with low ambient control valves like headmasters.

    Since it was a hermetic, I *assume* that you have to recover the entire charge and pulled a vacuum afterwards. Any chance of non-condensibles in the system?

    Another thing to look at would be a cracked or broken dip tube in the receiver. That'll kick your butt sometimes. Torch it and see where the actual level is while watching the sightglass.
  9. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    I recovered 10 lbs, and the vac was good. The rec should be full correct
  10. Y7turbo

    Y7turbo New Member

    Messages:
    9,438
    Location:
    Illinois
    When the head pressure was real high, did you notice if the condenser coil was warm or not?
  11. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    Not as far as touching it but I did notice the discharge air didn't seem to indicate excessive heat load. I did feel the rec and it was hot
  12. Y7turbo

    Y7turbo New Member

    Messages:
    9,438
    Location:
    Illinois
    If your pressures are real high, but your condenser isnt hot, it would indicate the headmaster bypassing the coil when it shouldn't be.

    Even if it was overcharged, during high head pressures the headmaster should have the hot gas port closed and full flow should be going through the condenser so the coil should be hot.
  13. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    Thanks for the info
  14. frozensolid

    frozensolid Psychologist's Dream

    Messages:
    9,895
    Location:
    Earth
    Why would you even need a head master in Texas?
  15. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    You tell me
  16. frozensolid

    frozensolid Psychologist's Dream

    Messages:
    9,895
    Location:
    Earth
    I can't think of any.
  17. Y7turbo

    Y7turbo New Member

    Messages:
    9,438
    Location:
    Illinois

    I think they go below 70 degrees once in every 10 years. :D
  18. Texas-Tech

    Texas-Tech stranger*

    Messages:
    9,339
    Location:
    duhh
    I think the condenser was made by yankees:cheers: