trane rtaa 150 ton chiller

Discussion in 'Commercial' started by nh33fan, Jan 18, 2012.

  1. Offline

    nh33fan Senior Member

    Message Count:
    438
    Likes Received:
    0
    Location:
    Lake Wales Fl.
    Have a 150 ton trane rtaa chiller with 2 circuits. Getting air code 1A9 on circuit 1 which says there a problem with exv valve replaced wire harness and checked all connection on board still getting error code. Took wire harness from circuit 2 and plugged it into circuit 1 at exv valve and get no error code when doing the exv test. however hooked circuit 1 from board to circuit 2 valve and get error again. both vales are working because I can here them operating but which ever valve is plugged into circuit 1 plug on board error code occurs, can plug either valve to circuit 2 plug and no errors occur Is it possible the 1U3 board is bad or any other suggestions. Thanks.
  2. Online

    Chrishvacman supercalifragilisticexpialidocious member*

    Message Count:
    1,272
    Likes Received:
    14
    Location:
    Fl
    Sounds like 1U3
  3. Online

    Airmechanical U n i v e r s a l - M o d e r a t o r

    Message Count:
    1,658
    Likes Received:
    15
    Location:
    cookeville,tn.
    i would speculate that the EXV driver board for the faulty circuit is fried